Installer
- DesMoines, Washington
We are installing an equipment rack on the second floor of Building powered by two 30 Amp Single Ø 120 VAC circuits.
The equipment rack has a power distribution unit which provides 48 VDC power through cables in a Cable chase to Touch Screen equipment on an Observation Deck on the top of the building 5 floors up.
I believe the 48 VDC power cabling should be in MC cable. However because the NEC Code doesn’t directly point to this guidance, I can’t get people to listen.
Starting with Article 720 “Circuits and equipment Operating at less than 50 VDC”, if you’re not an Electrical, you really have to dig into the code to find this guidance (look at the tree below; it isn’t easy.)
The requirement for MC cable isn’t easy to find in the NEC Code. Its buried under Photovoltaic PV systems. I’m probably going to get pushback because it’s under Photovoltaic Systems. Can I get some concurrence that this requirement for MC cable applies for a non PV application?
Thank you in Advance
Respectfully
RC on behalf of JP and AA
Respectfully
(G) Photovoltaic System Direct Current Circuits on or in a Building. Where PV system dc circuits run inside a building,
they shall be contained in metal raceways, Type MC metal-clad cable that complies with 250.118(10), or metal enclosures from
the point of penetration of the surface of the building to the first readily accessible disconnecting means. The disconnecting
means shall comply with 690.13(B) and (C) and 690.15(A) and(B). The wiring methods shall comply with the additional
installation requirements in 690.31(G)(1) through (4).