J jbolen Senior Member Nov 2, 2023 #1 I have project where the contractor inquiring if normal power MC cable and can be installed in same cable tray as MC cable emergency power.
I have project where the contractor inquiring if normal power MC cable and can be installed in same cable tray as MC cable emergency power.
ron Senior Member Location New York, 40.7514,-73.9925 Nov 2, 2023 #2 700.10 says entirely independent of other wiring, so I typically consider that the supports need to be independent.
700.10 says entirely independent of other wiring, so I typically consider that the supports need to be independent.