adalewhite
Master Electrician, Electrical Design, Veteran
- Location
- Georgia
- Occupation
- Licensed Electrician, Electrical Designer, A&E PM
(D) Use. Transfer equipment shall supply only emergency loads.
Does the paragraph above apply stricly to an emergency system that employs transfer equipment?
For instance it is clear that a system with both a computer room (optional) and emergency egress lighting served from a generator would require a transfer switch for each system. However, when you have a building and the entire facility is backed up by a generator would a transfer switch be required to isolate the legally required emergency systems?
700.5(B) seems to answer the question by allowing the alternate power source to supply emergency, legally required, and optional system loads " where automatic selective load pickup and load shedding is provided to ensure adequate power to (1) the emergency circuits, (2)the legally required standby circuits, and (3) the optional standby circuits, in that order of priority." There is also the requirement for a temporary generator whenever the emergency generator is out of service.
So let's say we have a facility where the existing emergency lighting is battery ballast without a separate emergency circuit. The client desires the entire facility to be backed up with a new genset. We know from experience the maintenance of the battery ballast will no longer take place since the generator is picking up the entire facility. With that in mind do I now also have to design the new system to provide separate circuits to provide the required level of emergency lighting and power?
Does the paragraph above apply stricly to an emergency system that employs transfer equipment?
For instance it is clear that a system with both a computer room (optional) and emergency egress lighting served from a generator would require a transfer switch for each system. However, when you have a building and the entire facility is backed up by a generator would a transfer switch be required to isolate the legally required emergency systems?
700.5(B) seems to answer the question by allowing the alternate power source to supply emergency, legally required, and optional system loads " where automatic selective load pickup and load shedding is provided to ensure adequate power to (1) the emergency circuits, (2)the legally required standby circuits, and (3) the optional standby circuits, in that order of priority." There is also the requirement for a temporary generator whenever the emergency generator is out of service.
So let's say we have a facility where the existing emergency lighting is battery ballast without a separate emergency circuit. The client desires the entire facility to be backed up with a new genset. We know from experience the maintenance of the battery ballast will no longer take place since the generator is picking up the entire facility. With that in mind do I now also have to design the new system to provide separate circuits to provide the required level of emergency lighting and power?