Isn't there an exception somewhere in article 701 that allows you to use a single transfer switch that feeds the (3) different load types when the load is under a certain kW/kVA ? Application is a surgery suite with office loads.
You are thinking of the Essential Electrical Systems requirements in Article 517.
Thanks Dave, you are right, thats exactly what I was thinking of.
So im thinking 517.30 diagrams would apply to this installation. Not Article 700/701.
Not quite. I had missed the connection with the hospital for this question. So let's set that (i.e., 517) aside for a moment and talk about your basic residential, commercial, or industrial facility. 700.5(D) tells me that I can't use one transfer switch to serve emergency loads and also to serve either legally required or optional standby loads. However, what tells me I can't use one transfer switch to serve both legally required and optional standby loads? I have always used separate ATSs for these two systems, but what tells me I must?Charlie: I think you are looking for 700.5 (D).
Currently we are planning on a single generator with a single transfer switch that feeds (3) separate panels; Life Safety (emergency lights), Critical (Operating Room Circuits), and standard loads (misc. lights/receptacles). This is only for a 35 kVA generator. Had the load been 150+ kVA than we would have had 3 separate transfer switches for the 3 different panels. As far as I know, this is code compliant.
Not quite. I had missed the connection with the hospital for this question. So let's set that (i.e., 517) aside for a moment and talk about your basic residential, commercial, or industrial facility. 700.5(D) tells me that I can't use one transfer switch to serve emergency loads and also to serve either legally required or optional standby loads. However, what tells me I can't use one transfer switch to serve both legally required and optional standby loads? I have always used separate ATSs for these two systems, but what tells me I must?
And the NEC is not going to help you figure that out. The NEC defers that decision to other authorities.I have a hard time trying to decipher which loads are 700, and which are 701.
My understanding is that article 700 and 701 would still apply to the respective branches.
Per 517.26, Article 700 only applies to the life safety branch, and 701 does not apply to Article 517 installations.Hi. Quick (and late question), why do articles 700 and 701 apply to the respective branches outlined in article 517 (life safety, critical and equipment)?
However, what tells me I can't use one transfer switch to serve both legally required and optional standby loads? I have always used separate ATSs for these two systems, but what tells me I must?
701.4 Capacity and Rating
A legally required standby system shall have adequate capacity
and rating for the supply of all equipment intended to be operated
at one time. Legally required standby system equipment shall be
suitable for the maximum available fault current at its terminals.
The legally required standby alternate power source shall be
permitted to supply both legally required standby and optional
standby system loads under either of the following conditions:
(1) Where the alternate source has adequate capacity to handle
all connected loads
(2) Where automatic selective load pickup and load shedding
is provided that will ensure adequate power to the legally
required standby circuits
Yes, now I'm having Deja-vu. I also thought that was a requirement, but then realized its not in 701 or 702. So it doesn't apply to legally required or optional standby systems. However, it does apply to COPS, which seems odd to me.
I have a hard time trying to decipher which loads are 700, and which are 701.