Hi Guys, I'm still working on that seminar presentation for Emergency and Standby Systems. Article 705 describes the rules for power sources in parallel. Would this apply to separately derived or non-separately derived systems?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I would think that by definition, 705 is talking about NON-separately derived systems. A separately derived system would have no direct electrical connection to supply conductors in another system.

705 describes taking two systems and connecting the directly together so they operate in parallel.
 