Article 727 and Industrial Machines

Status
Not open for further replies.

harmon.konrad

Member
Location
Washington State
Occupation
Electrical Engineer
I have been building industrial automation equipment for 6 years now and finally bumped into this gem of an article.

Cable trays and cable tracks carry both ITC cable and TC cable from the cabinet to the motor. Why is this allowed if 727 specifically says you can't install ITC next to any cable of a power circuit?

I this point I have just confused myself. I know we do it. Inspectors buy it off. Everyone in industry does it.
 

harmon.konrad

Member
Location
Washington State
Occupation
Electrical Engineer
NFPA 79.13.1.3 says you can put conductors of different circuits next to each other as long as they don't impair function and the outside insulation rating is that of the highest voltage conductor.

I think I found it.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Is this provided by the industrial machine manufacturer? If not, it would be my opinion that the rules in NFPA 70 and not NFPA 79 apply to that wiring. See NFPA 79, 1.4.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Are you installing the system? Even if you are, the installation may fall under section 1.4 in NFPA 79, and require compliance with the NEC.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Don and I were typing at the same time. If the cable tray is external to the control cabinet, doesn’t the NEC apply?
 

harmon.konrad

Member
Location
Washington State
Occupation
Electrical Engineer
There is a lot of debate where the lines are drawn. We make factories and we make corded equipment. Depending on the customer and the inspector they decide ultimately what they want us to follow. Hazloc stuff gets a bit more restrictive falling on the NFPA 70 side. NFPA 79 specifically ignores Hazloc and says refer to 70. What happens in my experience is you end up having to follow the strictest of both.

We always do the installation. Everything I install more or less falls under the exception under 1.4 if I interconnect anything. I think the exception also answers Tom's question. Our "field wiring" is integral to the machine and often goes through movement axis in energy chains.
 