hello all,
so i am project manager for a company that does a lot of work with OEM facilities, we mainly build E-houses for the control and protection side of the grid.
my question is. The contractor that we are working with wants us to run #12 and #10 SIS wire with 125VDC in wire basket from relay panel to relay panel but according to article 392.10(B)(1)(a) the smallest single conductor that is to be run is a 1/0awg cable ratted for cable tray. that being said the contractor is stating that because they are putting these buildings on the utility grid they do not have to abide by the NEC is there any better clarification on this article that i can argue with because i dont think its legal to run single #12 and #10 SIS wire in a cable tray or wire basket
so i am project manager for a company that does a lot of work with OEM facilities, we mainly build E-houses for the control and protection side of the grid.
my question is. The contractor that we are working with wants us to run #12 and #10 SIS wire with 125VDC in wire basket from relay panel to relay panel but according to article 392.10(B)(1)(a) the smallest single conductor that is to be run is a 1/0awg cable ratted for cable tray. that being said the contractor is stating that because they are putting these buildings on the utility grid they do not have to abide by the NEC is there any better clarification on this article that i can argue with because i dont think its legal to run single #12 and #10 SIS wire in a cable tray or wire basket