Can't find the article that allows a 3 wire to be run to a 240vac circuit to take a 120vac off of one leg for, say, an a/c condenser to satisfy the 25' rule. :?:?
As long as there is proper overcurrent protection on receptacle (many AC units have higher then a 20 amp breaker, even if allowed to have 12 AWG supply conductors) and the receptacle is not tied to the load side of the disconnect it is fine.That's now a closed thread and I can see why:happyyes: I'm talking about a 20a, 240vac feeding a a/c condenser.
To comply with a receptacle being no more than 25' from the unit, can you run a 12-3, and use one leg and the neutral to satisfy the rule? They make pull out disco's that incorporate a GFCI within the enclosure. Just wondering what section it's in.
They make pull out disco's that incorporate a GFCI within the enclosure.
Does it require two circuits if the there is a 20 amp supply circuit? You can't tap to the receptacle via the line side lug, but could use a wire nut or other device.Like this one, that requires two circuits?
That's now a closed thread and I can see why:happyyes: I'm talking about a 20a, 240vac feeding a a/c condenser.
To comply with a receptacle being no more than 25' from the unit, can you run a 12-3, and use one leg and the neutral to satisfy the rule? They make pull out disco's that incorporate a GFCI within the enclosure. Just wondering what section it's in.
Did it require a separate circuit or just individual conductors to land on the line side of the disconnect? Which is the general rule anyway unless the terminals are identified for multiple conductors.I inspected an Eaton AC disconnect with a GFCI receptacle and it required a separate 120V circuit for the GFCI receptacle.
210.23(A)(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires, shall not exceed 50 percent of the branch circuit ampere rating where lighting units, cord-and-plug connected utilization equipment not fastened in place, or both, are also supplied.
Unless the unit rating is less than 10 amps, it wouldn't be permitted.
I inspected an Eaton AC disconnect with a GFCI receptacle and it required a separate 120V circuit for the GFCI receptacle.
Did it require a separate circuit or just individual conductors to land on the line side of the disconnect? Which is the general rule anyway unless the terminals are identified for multiple conductors.
If the supply is protected by a 15 or 20 amp OCPD, NEC allows the receptacle to be on the AC circuit