Exactly how are they related, if at all?
This is not my scenario:
I would suspect this of being a violation of 700.10(B). I don’t think it would satisfy the Exception to sub paragraph (5)(b), in that I doubt the 600 amp and 400 amp breakers could be selectively coordinated. Let us assume, for the present, that they cannot.
This is my scenario:
517.30(C)(1) has rules about separation of wiring. But they are not as detailed or explicit as we see in article 700. Am I seeing a violation? Can you even cite a violation of article 700 in a hospital, or does it even apply at all?
This is not my scenario:
- Existing commercial building.
- Existing backup generator, with 600 amp breaker at the source.
- Existing “emergency switchboard.” It has two 400 amp breakers.
- One breaker serves “emergency” (Article 700) loads via an ATS.
- The other breaker serves “optional standby” (Article 702) loads via a separate ATS.
I would suspect this of being a violation of 700.10(B). I don’t think it would satisfy the Exception to sub paragraph (5)(b), in that I doubt the 600 amp and 400 amp breakers could be selectively coordinated. Let us assume, for the present, that they cannot.
This is my scenario:
- Same as above, except that it is a hospital.
- Same distribution as above, except that one ATS serves “critical branch” loads and the other serves “equipment branch” loads.
517.30(C)(1) has rules about separation of wiring. But they are not as detailed or explicit as we see in article 700. Am I seeing a violation? Can you even cite a violation of article 700 in a hospital, or does it even apply at all?