Looking for articles pertaining to the application of generators with down stream UPS's. Anybody know of any?
Mike
Mike
mshields said:Thanks for all of the input. Have downloaded several articles from the sources you suggested.
Ron - you asked more specifically what I was looking for. I'm writing a paper on why generators need to be oversized to handle down stream UPS's. I've found that while it's common knowledge that this is so and that the gen sizing programs most of us use keep us out of trouble, an understanding of what drives the concern is less common. In general, I'll be discussing how current harmonics interact with the high impedances of generators to create high levels of voltage harmonics and the troubles this can cause.
Frankly, I'm still toying around with whether or not this scope is too narrow or not and am of an open mind as to what exactly the paper transpires to be. Hence the interest in a broad range of subject matter provided they have to do with the interaction of these two devices.
Thanks,
Mike
mshields said:Hmmm - very interesting. So there are two scenario's that can result in the UPS toggling between gen power and battery power:
1. High current harmonics interacting with high reactance of genset results in high voltage distortion which the front end of the UPS rejects.
2. Inrush you describe above resulting in a voltage dip which the front end of the UPS rejects.
True?
And let me ask you this, how do the inrush characteristics of an SCR front end compare with that of an IGBT front end?
Mike