Technically Still Ungrounded: Even with the artificial neutral and HRG, the system is technically considered ungrounded according to most electrical codes. The high resistance limits the fault current, allowing detection without solidly connecting the neutral to earth.
The code typically doesn't prohibit disconnecting the artificial neutral. Since the HRG limits fault current, disconnecting the neutral shouldn't create a safety hazard during maintenance. However, it would render the ground fault detection system inoperable. Disconnecting the neutral defeats the purpose of the ground fault detection system. Without fault current flowing through the HRG and pulsing sleuth, a ground fault might go undetected, potentially leading to equipment damage or safety risks.
NEC Code References:
- Article 250: Grounding and Bonding Systems
- Article 400: Flexible Cables and Fittings (covers grounding of neutral conductors)
The Canadian Electrical Code (CEC) uses similar grounding principles to the NEC, but there might be some variation in terminology or specific requirements. Here are the relevant sections of the CEC to explore for your situation:
- Section 10-000: Grounding and Bonding
- This section outlines the general requirements for grounding and bonding electrical systems in Canada.
- Section 10-210: Grounding of System Neutral Conductors
- This section details how to ground neutral conductors in different system configurations. While it primarily focuses on solidly grounded systems, it provides a general framework for understanding grounding principles.
- Section 10-220: High-Impedance Grounded (HIG) Systems
- This section specifically addresses High Impedance Grounded (HIG) systems, which is the Canadian equivalent of High Resistance Grounded (HRG) systems used in the US. It outlines the conditions for using HIG systems and the grounding requirements.