These are located in shop classrooms. Remote open, manual close is an acceptable operation. I was asking more if anyone has an opinion about one option over the other.Those switches were often used where automatic or remote operation was desired, such as for energy management. A shunt trip breaker opens remotely, but it requires local manual intervention to close.
The panels are being replaced.Does it work reliably?
Ahh... thats a good thought. This would be connected to an emergency power off switch, so I don't think that it would be a daily operation. At least, in my trade school days, we never hit the e-stop hahaha.Depending on the size of the breaker, daily shunt trip operation could mean a relatively short breaker life.
The last school redo I did, they operated the 'power off' circuit as a means of shutting down the work shops/labs when they were not occupied. They were not really for emergencies as none of the buttons were mushroom head, nor were they conveniently located.Ahh... thats a good thought. This would be connected to an emergency power off switch, so I don't think that it would be a daily operation. At least, in my trade school days, we never hit the e-stop hahaha.
Ahhh... interesting.The last school redo I did, they operated the 'power off' circuit as a means of shutting down the work shops/labs when they were not occupied. They were not really for emergencies as none of the buttons were mushroom head, nor were they conveniently located.
You would have to install it in another can, that particular contactor is made to fit in a panel board, most other brands of contactors that size will not fit if you want to put the cover back on. LOL!
Yes, but the problem will remain. The CAN and/or the wall space for the can is shallow, and modern latching contactors for that size load (assuming 100A) are (probably) no longer than shallow.The guts are going to be replaced.![]()
good to know... Thanks!They still make that contactor, we have several customers that use them.
I designed a circuit like that for big box tool rental repair shops, interlocked it with the exhaust fan too, so if the fan quit working for any reason (belt broken, motor quit, etc) it would shut off all the tools in the room including the air compressor. They worked on gas powered equipment like pressure washers in there.One of the reasons for having a contactor switch the shop power is to prevent any automatic restart of tools or machines left on when the power went out. Make sure the contactor is electrically held and not mechanically held.
I designed a circuit like that for big box tool rental repair shops, interlocked it with the exhaust fan too, so if the fan quit working for any reason (belt broken, motor quit, etc) it would shut off all the tools in the room including the air compressor. They worked on gas powered equipment like pressure washers in there.
For lighting loads, you could have just taken the OL relay out altogether.A company I worked for a long time ago had a dedicated buyer for their projects, I went out to a grocery store we were wiring to hook up the lighting controls. Opened up the contactor boxes, every one of them had a large motor starter instead of a lighting contactor! I called and told him he ordered the wrong thing. He said make it work. I put in the largest overloads they would take, and hoped for the best...........well, it worked for a week or two, then the overloads burned up! LOL!