FYI, The DoD has just mandated that they will follow ASHRAE 90.1 2013 for sustainability and mandatory requirements. This locks in the receptacle controls in under federal law (EPACT 2005) for DoD facilities. I formally submitted to ASHRAE in 2012 using the 24/7 reasoning for exempting the offices being controlled if we only had required receptacles. At the time we only put in enough receptacles or connections to power the computers and printers which by federal mandate have to be powered ON and connected to the network whenever possible. We cannot switch them off with the sensors as ASHRAE intended. I was straight out rejected. I went to headquarters and requested them to remove the paragraph in the criteria and was told it was inexpensive and a good idea to follow along. Before this last mandate, I could exempt the controlled receptacles in break rooms and conference rooms from the Criteria. Now it is not an option. I now add double the needed receptacles and route the extra receptacles through a relay that has a coil controlled by the room sensor (No need to worry if 120V or 277V). We now can only feed 6 workstations from one system furniture power line (limits of the channel space in all manufacturers). It is known these switched receptacles are not getting used. Just when you though it could not get worse on this topic. This is being done on projects where most engineers are trying to get our military usable spaces with skeleton budgets. Personally I see this as a cowards way to justify sustainable design.