I am currently installing "on-off" valves in a chemical plant and will be using ASi bus for control. This is a two wire comunication to intelligent devices and the devices obtain their power from the two wire buss (about 30vdc). The question I have is in regard to the proper sealing of the cables for both Class I Div. 1 and Class I Div. 2 Group C &D locations. Most of the manufacturers of the cables and terminators provide instructions/guidelines for these area class installations. For Div. 2 it is essentially to use factory made cables and then have a locking mechanism on the hazardous area side so that the cable cannot be removed under power without some effort. For Div. 1 it is to use a "special Class I div. 1" cable and fitting assembly. The problem is the cable is flexible and essentially "shipboard" cable. My interpretation of the NEC code is that "shipboard" cable is not an approved wiring method for class I Div. 1. Has anyone had experience with this type of buss network and the use of "shipboard" cable in a Class I div. 1 environment? Is there an exception or code article that allows the use of this cable in Div. 1 areas?