ASK:CABLE TRAY for Service of dwelling units in a apartment building

Status
Not open for further replies.

rojhan123

Member
Location
Philippines
Good Day. I have 14 units(condo units) supplied in the same feeder can i put them all in the same cable tray? there will be 2-14mm2 1-8.0mm2 THHN wires per unit. If yes what size of cable tray should i used for this setup or if not what would you recommend for me to use.Thank you
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Take a look at 392.3. I believe you will find the smallest single conductor that can be use is 1/0 and single conductors are restricted to industrial establishments.
 

rojhan123

Member
Location
Philippines
So you mean Sir I cannot used the cable tray as a raceway for service conductors of each unit in the building?please enlighten me with these. Thank you
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
NEC 2014 art.392.10 (A) Wiring Methods. The wiring methods in Table 392.10(A) shall be permitted to be installed in cable tray systems under the conditions described in their respective articles and sections.
Unfortunately, no THHN,THNW and other single core insulated conductor -without an external jacket- is registered here.
As a compromise you have to run-at first- the cable through ENT conduit and then in cable tray.
You may use metal or nonmetallic wireway instead of [Art 376 or 378] for these cables.
 