I was sent the drawings which include a tittle sheet, architectural and canopy. No E sheets panel schedules no spec no nothin nadda.
Copied email from GC
"Scope of work includes???"
"Replace 33 light lens and lamps in 2x4 fixtures.
Provide wire and install temp power to Kiosk in front of store.
Supply and install power pole for Condiment Island.
Supply and install one 208v outlet for Deli case.
Disconnect power and data from existing cashier counter.
Supply and install under-slab conduits to new cashiers counter.
Project starts on Nov 23 and completes Dec. 11 I also have another Arco in Stockton starts the same day."
Im just amazed with the lack of info..sorry had to vent!
My reply was:
1. Replace 33 light lens and lamps 2X4 fixtures
A. Light lens Spec?
B. Owner Supplied?
C. Lamp Spec
D. Owner Supplied?
2. Temp power to Kiosk
A. Kiosk Load / Spec?
3. Power Pole to Condiment Island Spec Sheet?
A. Circuit Size
B. Voltage
C. Panel Schedule
4. 208VAC Deli Case Outlet
A. Current Size?
5. Disconnect power and data from (e) cashier counter
A. Demo Circuit to panel?
6. Supply and install under-slab conduits to new cashier counter
A. Conduit QTY?
B. Conduit Size?
C. Circuit Size?
D. Slab Cut / GC or Sub?
E. Slab repair GC or Sub?
F. Panel Schedule?
Notes: Air Curtain Power, Fuel Equipment Relocation, Exit Signage, No E-Drawings, Fixture Schedule, Panel Schedules.
Copied email from GC
"Scope of work includes???"
"Replace 33 light lens and lamps in 2x4 fixtures.
Provide wire and install temp power to Kiosk in front of store.
Supply and install power pole for Condiment Island.
Supply and install one 208v outlet for Deli case.
Disconnect power and data from existing cashier counter.
Supply and install under-slab conduits to new cashiers counter.
Project starts on Nov 23 and completes Dec. 11 I also have another Arco in Stockton starts the same day."
Im just amazed with the lack of info..sorry had to vent!
My reply was:
1. Replace 33 light lens and lamps 2X4 fixtures
A. Light lens Spec?
B. Owner Supplied?
C. Lamp Spec
D. Owner Supplied?
2. Temp power to Kiosk
A. Kiosk Load / Spec?
3. Power Pole to Condiment Island Spec Sheet?
A. Circuit Size
B. Voltage
C. Panel Schedule
4. 208VAC Deli Case Outlet
A. Current Size?
5. Disconnect power and data from (e) cashier counter
A. Demo Circuit to panel?
6. Supply and install under-slab conduits to new cashier counter
A. Conduit QTY?
B. Conduit Size?
C. Circuit Size?
D. Slab Cut / GC or Sub?
E. Slab repair GC or Sub?
F. Panel Schedule?
Notes: Air Curtain Power, Fuel Equipment Relocation, Exit Signage, No E-Drawings, Fixture Schedule, Panel Schedules.