I have had a dialogue with our tenured chief inspector and would like assitance with this question for his assurance. We have a 100% concentric nuetral XLP primary cable entering a 300KVA, 3 phase, 12,470 volt primary, 120/208Y secondary, delta wye configured transformer. The transformer we are replacing was configured as a wye-wye previously. We are of the belief that since we have a 100% concentric nuetral (and not a 1/3 full concentric nuetral), we do not need a nuetral on the secondary and only need to ground the X0 with a #6AWG, thus using a 3 wire cable and not a 4 wire cable on the secondary. We know to leave the nuetral unconnected on the primary since we are concerting from a wye-wye to a delta-wye and installing a delta-wye pad mounted transformer.
Would you agree?
Would you agree?