Assuming A Gound Wire

Status
Not open for further replies.

JRSPARKY

New member
Electrical NEC Exam Preparation book page 213 #26 we are to assume an equipment ground conductor. Then on page 215 #2 we are not to assume a equipment ground conductor. Why the conflict between questions. Thank You, JRSPARKY
 

dcspector

Senior Member
Location
Burke, Virginia
NEC 250.118 allows these listed raceways to be EGC's on the other hand if you install an additional ( bare or green conductor) EGC then it must meet 250.119, 250.122. 250.148, etc.
 