ASTM 53 for underground RMC

Status
Not open for further replies.
Location
NC/SC
In a pinch and I need some short pieces of RMC for a feeder in a shallow trench. I went to a home improvement store and had them thread some ASTM 53 pipe. This inspector knows his stuff. Will it fly? Why?

Sent from my LGLS991 using Tapatalk
 

drktmplr12

Senior Member
Location
South Florida
Occupation
Electrical Engineer
I'm going to say it would be a violation because it wasn't designed to be used to physical protection and routing of conductors and isn't listed.

NEC 2011 344.2

344.2 Definition.
Rigid Metal Conduit (RMC). A threadable raceway of
circular cross section designed for the physical protection
and routing of conductors and cables and for use as an
equipment grounding conductor when installed with its integral
or associated coupling and appropriate fittings. RMC
is generally made of steel (ferrous) with protective coatings
or aluminum (nonferrous). Special use types are red brass
and stainless steel.
344.6 Listing Requirements. RMC, factory elbows and
couplings, and associated fittings shall be listed.


From American Piping Products
:

ASTM A53 pipe
(also referred to as ASME SA53 pipe) is intended for mechanical and pressure applications and is also acceptable for ordinary uses in steam, water, gas and air lines. It is suitable for welding and for forming operations involving coiling, bending, and flanging, subject to certain qualifications.

 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Among other things, fluid transport operations do not require the inside of the pipe to be smooth (mitigating scuffing or penetration of wire and high pulling force.)
Think of internal weld seams, for example.
 