ryan_618
Senior Member
- Location
- Salt Lake City, Utah
I did an inspection at a house yesterday that I failed to the service disconnect having an insufficient AIC rating. I used the infinite buss primary method at the transformer (located very close to the house) and came up with 18,000 available at the transformer. Using the point-to-point method, I then calculated 13,500 available at the service, which consisted of a main circuit breaker rated 10,000 AIC.
I spoke with a gentlmen from UL this morning about an unrelated topic, and this topic somehow got brought up. He then told me that the asymetrical fault current is about 1.414 times the symetrical fault current, so if my calculations were based on the asymetrical fault current, my breaker might be alright, because the breaker will be rated higher than 10K asymetrical, and will be rated 10K symetrical.
I hate to say it, but I don't really understand the difference here
When doing a fault current calculation, are we calculating the symetrical or the asymetrical current? What is the difference? How long does the asymetrical fault last in comparison to the symetrical? Are we talking half a cycle? 5 cycles????
Thanks
I spoke with a gentlmen from UL this morning about an unrelated topic, and this topic somehow got brought up. He then told me that the asymetrical fault current is about 1.414 times the symetrical fault current, so if my calculations were based on the asymetrical fault current, my breaker might be alright, because the breaker will be rated higher than 10K asymetrical, and will be rated 10K symetrical.
I hate to say it, but I don't really understand the difference here
When doing a fault current calculation, are we calculating the symetrical or the asymetrical current? What is the difference? How long does the asymetrical fault last in comparison to the symetrical? Are we talking half a cycle? 5 cycles????
Thanks