At what distance is voltage drop a concern for 480V circuits?

Mumbaigirl

Member
Location
USA
Occupation
Electrical Engineer
Hello,
Is there a general rule of thumb for 480V circuits without having to actually calculate for the 3% voltage drop?

Thank you,
Jui
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Voltage drop is dependent upon the load. If you have a 20 amp circuit and you are only drawing 2 amps then you could go a much greater distance than you could if you were drawing 18 or 20 amps.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I don't believe voltage has anything to do with the voltage shop formula. Either way the 3% voltage drop is only required for fire pumps. Otherwise the 3% is a recommendation
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
As stated, voltage drop is only dependent on circuit impedance and load current.

But, the relative effect of a given voltage drop is dependent on the circuit voltage.

A given absolute amount of drop is a greater percentage of a lower circuit voltage.

Thus, the higher the voltage, the less detrimental is a given amount of voltage drop.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The rule of thumb that I have heard, is you don't have to look close at voltage drop until the length of the circuit is close to the voltage of the circuit. So for a 120 volt circuit, 100', and a 480 volt circuit, 450'.
 

Mumbaigirl

Member
Location
USA
Occupation
Electrical Engineer
The rule of thumb that I have heard, is you don't have to look close at voltage drop until the length of the circuit is close to the voltage of the circuit. So for a 120 volt circuit, 100', and a 480 volt circuit, 450'.
Thank you so much! I appreciate it.
 

Mumbaigirl

Member
Location
USA
Occupation
Electrical Engineer
As stated, voltage drop is only dependent on circuit impedance and load current.

But, the relative effect of a given voltage drop is dependent on the circuit voltage.

A given absolute amount of drop is a greater percentage of a lower circuit voltage.

Thus, the higher the voltage, the less detrimental is a given amount of voltage drop.
Thank you so much! I appreciate it.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The rule of thumb that I have heard, is you don't have to look close at voltage drop until the length of the circuit is close to the voltage of the circuit. So for a 120 volt circuit, 100', and a 480 volt circuit, 450'.
I should have stated the % of the drop will vary with the voltage. For instance 120v with a 12 volt drop is 10%. While at 480V with a 12v dop is only
2.5% drop
 