Substantiation: The Ampere/Voltage rating needs to be addressed as there are
coin-operated 30 A, 250V electric clothes dryers that, possibly were not
intended to be included. The definition is needed to distinguish that you put a
coin into the slot and you receive merchandise or a product. Many cordconnected
coin-operated machines do not vend merchandise or a product,
instead they offer a service such as clothes washers, clothes dryers, ATM
machines, ice machines (no coin needed), slot machines (some are cord-and
plug-connected; of course, you get nothing back). The intent of this proposal is
to give the Code-Making Panel some thoughts toward clarifying this section for
2008.
Panel Meeting Action: Accept in Part
Revise 422.51 to read as follows:
Cord-and-plug-connected vending machines, manufactured or remanufactured
on or after January 1, 2005, shall include a ground-fault-circuitinterrupter
as an integral part of the attachment plug or located within 300 mm
(12 in) of the attachment plug. Older vending machines manufactured or
remanufactured prior to January 1, 2005, shall be connected to a GFCIprotected
outlet. For the purpose of this section, the term ?vending machine?
means any self-service device that dispenses products or merchandise without
the necessity of replenishing the device between each vending operation and
designed to require insertion of a coin, paper currency, token, card, key, or
receipt of payment by other means.
Add FPN to read as follows:
FPN: For further information, see ANSI/UL 541-2005, Standard for
Refrigerated Vending Machines, or ANSI/UL 751-2005, Standard for Vending
Machines.
Panel Statement: The panel rejects the deletion of re-manufactured vending
machines as well as the branch circuit limitations. There is no substantiation
for not providing the same level of safety for vending machines that are on
branch circuits of greater than 20 amperes or 120 v.
The panel accepts the submitter?s statement defining vending machines as
modified.
Number Eligible to Vote: 14
Ballot Results: Affirmative: 14