The situation is at my facility they are asking me to take a ATS that was used on a building and use it on another. My administrator hasn't responded to me but my main question is the current location it was used at was 277/480 3 phase. The new location is 120/208 3 phase. Can I utilize that ATS on the diffrent voltage? I haven't found anything saying no. But I am second guessing my knowledge on this.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Well, perhaps yes, but no anyway.

Voltage ratings are based on the component's insulation system's ability to prevent leakage current from the current-carrying metal to the outside world. Since the ATS can handle 480 volts without leakage current, it should easily handle 208 volts.

My concern is the method that the ATS uses to detect a loss of voltage on the normal side. Would it not transfer when it sees only 208 volts available?
 

GnomeDaddy

Member
Location
Tacoma, WA
Occupation
Electrical Supervisor,
Well, perhaps yes, but no anyway.

Voltage ratings are based on the component's insulation system's ability to prevent leakage current from the current-carrying metal to the outside world. Since the ATS can handle 480 volts without leakage current, it should easily handle 208 volts.

My concern is the method that the ATS uses to detect a loss of voltage on the normal side. Would it not transfer when it sees only 208 volts available?
I appreciate this, as I was looking at it I am able to adjust it. I am looking code wise, an the fact it is essentially using old equipment.
 

Birken Vogt

Senior Member
Location
Grass Valley, Ca
You will probably need to change the actuator coil as well. If it uses 480 volts to operate now. Often they have a different coil for 208 than 240 even. Off the cuff it is probably not worth it. Is this ATS very large and/or special?
 
It really depends on the ATS. I installed a 600 amp Thompson a couple years ago, you could change the voltage on it. There's usually nothing wrong with used equipment, and no code prohibition of it. I use used equipment frequently.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
You are still going to have to change hard part(s) that are voltage specific.
Not necessarily, the older Kohlers used step down transformers for the control solenoids and electronics. Residential grade transferswitches though, usually are line voltage on the solenoids or actuators. The transformer would be the only part changed. Or may be multi tap.
 