Raptor1963
Member
- Location
- Illinois
Looking for comment on this scenerio....1500kW 480VAC generator w/ 2500a MCB......3000a 480VAC Utility breaker in the ATS feeding the building load.
Got an ATS being fed from utility service and the emergency side fed from a generator....this is all housed in a weatherproof enclosure....the customer want to supply voltage to the enclosure accessories via tapping off the load buss connection.....there is a fused disconnect switch (65A fuses) feeding a single phase 480:240/120v transformer and load center....so using 240.21(1) tap rule & mounting the disconnect switch right beside the ATS, I would have to size the conductors not less than 1/10 the ampacity of the OC protecting the feeder conductors (300A). Questions is if I just use a 6" nipple out of the side of the ATS cabinet can i get away with rating the conductors in free air? If I could justify free air then I could get away with a 200A fused disconnect switch that would take the 3/0awg cable rated in free air = 310A....Otherwise I would have to jump up to a 400a DS to have the properly rated lugs and bend radius for 350kcmil cable = 310A in conduit....comments????
Got an ATS being fed from utility service and the emergency side fed from a generator....this is all housed in a weatherproof enclosure....the customer want to supply voltage to the enclosure accessories via tapping off the load buss connection.....there is a fused disconnect switch (65A fuses) feeding a single phase 480:240/120v transformer and load center....so using 240.21(1) tap rule & mounting the disconnect switch right beside the ATS, I would have to size the conductors not less than 1/10 the ampacity of the OC protecting the feeder conductors (300A). Questions is if I just use a 6" nipple out of the side of the ATS cabinet can i get away with rating the conductors in free air? If I could justify free air then I could get away with a 200A fused disconnect switch that would take the 3/0awg cable rated in free air = 310A....Otherwise I would have to jump up to a 400a DS to have the properly rated lugs and bend radius for 350kcmil cable = 310A in conduit....comments????