Going by a decrement curve an Emergency generator can produce 3x the rated current for a 3 phase fault 15 seconds, and 5 times the rated current for a L-G fault for 5 seconds.
1,500kw generator is rated 1,800 amps FLC. x3 = 5,400 amps, x5= 9000 amps.
Going by time current curves it takes 5x the current to open an OCPD in 10 seconds, 7x in 5 seconds.
9000/7=1,200 amps
Would it be safe to infer a 1000-1,200 amp feeder limit on the emergency switchboard during design to aid in selective coordination?
As is I like to limit ATSs to 800 amps max.