Andre Proulx
Member
- Location
- Bon Conseil,Quebec,Canada
- Occupation
- retired Master electrician
hi, i like to fully understand the inner working of an generac ats model RXSC200A3 specialy why the full bridge on the coils also the limit switch
Thanks Birken. The DC voltage to the solenoid coils provides a greater pushing or pulling force vs AC during transfer of the main contacts. Your limit switch answer is correct. In a typical ATS the solenoids are designed for momentary operation (coil is wound for maximum force) and if a limit switch fails or the mechanism jambs, the solenoid coil stays energized and shorts out causing the solenoid and harness wiring to burn up. I have rewired many units; due to lack of maintenance the factory grease along with dirt dries up causing the mechanism to jamb in mid-position.All transfer switches seem to have a bridge rectifier on the coil(s), must run better on DC than AC.
One member on here ATSman may be able to answer better
The limit switch is there to break the pulling of the coil after the motion completes. Without the limit switch current will continue to flow in the coil and the coil dissipates 1 kw from my measurement, stuff will burn up quick like that.