ATS Neutrals

Status
Not open for further replies.

rayertz

Member
Location
USA
We have an Automatic Transfer switch. Normal power is from a breaker in the substation to a service disconnect switch then to a 480 to 480/277 transformer creating a neutral finally it ends up in the ATS for normal power.
We have a E-generator which is 480 / 277 with it's own neutral, all landing in the ATS for E-power.

My question is; in the ATS are the neutrals all tied to a common point in the ATS or should they ISOLATED?

Please see rough sketch attached.

Thanks
 

Attachments

  • ATS Sketch.pdf
    85 KB · Views: 1

rlundsrud

Senior Member
Location
chicago, il, USA
neutral

neutral

If the neutral isn't bonded at the generator then yes you can tie them together at the transfer switch. If it is bonded at the generator then you would need a 4 pole transfer switch and isolate the neutral.

Bob
 

iwire

Moderator
Staff member
Location
Massachusetts
If the neutral isn't bonded at the generator then yes you can tie them together at the transfer switch. If it is bonded at the generator then you would need a 4 pole transfer switch and isolate the neutral.

Code wise that is true, however if there is ground fault protection included the use of switched neutral switch is recommended.
 

ATSman

ATSman
Location
San Francisco Bay Area
Occupation
Electrical Engineer/ Electrical Testing & Controls
ATS GF Problems_Solutions

ATS GF Problems_Solutions

This may help
 

Attachments

  • ATS Ground-Fault Current Problems and Solutions.doc
    39 KB · Views: 2