We won a job just recently and the ATS's were 175A and now reduced to 125A via change order. They just got the order last week. I'm confused by the email the ATS vendor sent out saying no credit due to the size reduction. The client is expecting a credit and I would think going down to 125A would result in the ATS's being cheaper. Below is the response. Doesn't make sense to me.
The rating changes for the (3) ATSs is not going to impact the PO pricing since we already upsized all ATSs to accommodate the 65kAIC specific breaker WCR.
The rating changes for the (3) ATSs is not going to impact the PO pricing since we already upsized all ATSs to accommodate the 65kAIC specific breaker WCR.