ATS sizing

cppoly

Senior Member
Location
New York
If you have a 100 amp continuous load, is a 100 amp ATS sufficient or is the rating of the ATS required to be sized at 125%?
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
I’m installing a 48 kw right now with a 200 amp switch, and seems like I read it was limited to 85% or something like that, in the install manual? I was looking to make sure the lugs were rated for aluminum, so didn’t give it that much attention. It was service rated, so that may have been the reason.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
I work on this stuff daily and never noticed anything like that. Maybe I missed it but I generally read the books pretty well.
It may have been because it was a service rated switch, because of the main breaker that’s not in a regular T switch. The manual is at the job site, so I can’t look it up until I get back.
 
Top