I can't get my head around a system that I am currently inspecting to the point that I can say "no problem". Assistance will be appreciated.
(a) A new installation has a pad transformer feeding a 3000 amp MDP.
The system is 480/277 so my 3000 amp main is GF protected.
(b) A 400 amp feeder from MDP feeds a ATS. The ATS does not switch the neutral, therefore the generator is not an SDS and there is no N-G bond at the generator, but we do have a EGC to the generator.
(c) Now we add a fire pump with combination controller ATS. The transformer supply has a grounded conductor bonded to the service rated ATS.
The generator supply has no grounded conductor brought to the fire pump but an EGC bonded to the generator frame and ATS.
Two questions
(1) Is the above Code compliant ?
(2) Will the system as wired pose any conflict with the MDP being GF protected ?
(the few systems I have seen with a GF main have had ATS systems with a switched neutral)
(a) A new installation has a pad transformer feeding a 3000 amp MDP.
The system is 480/277 so my 3000 amp main is GF protected.
(b) A 400 amp feeder from MDP feeds a ATS. The ATS does not switch the neutral, therefore the generator is not an SDS and there is no N-G bond at the generator, but we do have a EGC to the generator.
(c) Now we add a fire pump with combination controller ATS. The transformer supply has a grounded conductor bonded to the service rated ATS.
The generator supply has no grounded conductor brought to the fire pump but an EGC bonded to the generator frame and ATS.
Two questions
(1) Is the above Code compliant ?
(2) Will the system as wired pose any conflict with the MDP being GF protected ?
(the few systems I have seen with a GF main have had ATS systems with a switched neutral)