Hi,
I have an ATS that has a utility 480VAC WYE feed on source one and a generator 480VAC WYE on source two. The systems downstream of the ATS are all 480VAC and do not require a neutral. (some motors, delta primary transformers and power supplies).
The ATS in question is a 4 pole ATS, it is configured for 3pole no neutral. The neutral from utility and generator are therefore not connected to the ATS. Instead the electrician tied them both together in the panel and are further not connected to anything else. The utility 480WYE transformer neutral is bonded to ground at the transformer, the generator neutral is also bonded to ground at the generator. Summarized, ATS has two sources, both sources have L1, L2, L3 terminated on the ATS. Neutral of both sources are tied together on a lug in the same panel.
I believe both neutrals should be terminated on the ATS and kept isolated from one another due to the generator neutral being separately bonded to ground, even if downstream of the ATS nothing is connected to neutral.
Would like to hear ya'lls thoughts and if there is any NEC code that this violates.
I have an ATS that has a utility 480VAC WYE feed on source one and a generator 480VAC WYE on source two. The systems downstream of the ATS are all 480VAC and do not require a neutral. (some motors, delta primary transformers and power supplies).
The ATS in question is a 4 pole ATS, it is configured for 3pole no neutral. The neutral from utility and generator are therefore not connected to the ATS. Instead the electrician tied them both together in the panel and are further not connected to anything else. The utility 480WYE transformer neutral is bonded to ground at the transformer, the generator neutral is also bonded to ground at the generator. Summarized, ATS has two sources, both sources have L1, L2, L3 terminated on the ATS. Neutral of both sources are tied together on a lug in the same panel.
I believe both neutrals should be terminated on the ATS and kept isolated from one another due to the generator neutral being separately bonded to ground, even if downstream of the ATS nothing is connected to neutral.
Would like to hear ya'lls thoughts and if there is any NEC code that this violates.