2008 NEC:
700.10(D)(3) Generator Control Wiring. Control conductors installed between the transfer equipment and the emergency generator shall be kept entirely independent of all other wiring and shall meet the conditions of 700.9(D)(1).
How do you explain the cable from Generac that has everything in one cable assembly?Take a look here:
Like 7D41 said those systems are only optional standby.How do you explain the cable from Generac that has everything in one cable assembly?
Standby and emergency generators have different requirements. Generally the Generac that allows for the "cable assembly" are sold for the standby generator.How do you explain the cable from Generac that has everything in one cable assembly?