StronerRich
Member
- Location
- Pella, Iowa, USA
I work for a large manufacturing company in Iowa with 4 plants around the state and have gotten conflicting answers from electrical inspectors on this application. We install equipment (480 VAC/30 amps or less) using the following method. Coming off a 600 amp buss duct with a 30 amp fusible buss duct switch we'll run IMC or EMT conduit to a deep 4-square metal box using 10 gage wire. The buss duct is grounded to the power distribution system and the metal 4-square box is attached to a metal ceiling truss using metal fasteners. The metal truss is attach to cross beams and columns which are attached to the building's grounded grid system. In the 4-square box we splice the conductors and ground wires and change over to a rated flexible cord drop which we run to the machine disconnect. The question is whether we have to bond the ground wire to the box. I have had an inspector say yes because of Article 250.148 and I have had an inspector say no that since the circuit is above 277V and there are no ringed knockouts used Article 250.97 says that the bonding jumper is not required. My discussions with the inspectors revolves around this point, the metal conduit provides a ground connection to the 4-square box and the grounded grid building system provides a second grounding source for the box what added safety factor does the bonding jumper get us? We do this with larger conductors up to 250 MCM (not the soft drops), but using large Hoffman type boxes as pull boxes with conduit in and out that might have splices in them do we us a bonding jumper in that case? Thanks