Re: attic addition
It's not clear from the OP if these new rooms are part of an attic renovation, or if the attic's just a convenient place for the proposed panelboard. Just a thought: If it's the latter, the attic has to have permanent stairs, an access hatch wouldn't satisfy 110-33(b).
As for derating: Assuming the load for OCPD selection is 60Amps and we're talking about a 120/240 3-wire panelboard feeder with 75C terminals and 90C conductors, #6 Cu has a 75C rating of 65Amps and its 90C rating is 75Amps. Even derated for a 45C ambient (for example, what they allow for normally-ventilated attics in L.A.) at 87%, that's 65Amps. So you'd be OK with a 60Amp CB protecting a #6 feeder to the panelboard.
If you're concerned with keeping the voltage drop to 2% in the feeder, #6 Copper at 60Amps, 120Volts is good for a run of 41-45 feet (depending on how you figure it). If you need a run of 65-72 feet, increase to #4 and if you need a run of 98-114 feet, increase to #2.
The minimum EGC for a 60A OCPD is #10 Copper, but if you increase the conductors for VD, then you have to increase the EGC as well. #4 conductors would need a #6 EGC and #2 conductors would need a #4.