• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

Auto stands generator

Status
Not open for further replies.

kylelee

Member
Location
多伦多
Here in Toronto, can I use a 24kw generator to feed an 200a panel? Or I must get a 48kw one? Or I need to put another small generator panel on side?


Sent from my iPhone using Tapatalk
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Generator should be sized for the expected load; it need not equal the service.

Look for info on load shedding.
 
Status
Not open for further replies.