I have a step-up auto transformer that feeds an elevator disconnect on it's secondary. The auto transformer goes from 208V, 3 phase to 480V, 3 phase.
The available fault current on the primary side of the autotransformer is 6,700 amps.
The transformer is 32 kVA and I'm assuming 1.5% impedance. The available fault current at the elevator disconnect needs to be below 5,000 amps.
I would assume that the high voltage side of the transformer would reduce my available fault current and I could calculate it the same way that I would calculate fault current for a step down transformer. My secondary (480V) side is showing 1,359 amps. In my eyes, this would allow me to meet the short circuit current rating of the 5,000 amps listed on the elevator equipment.
I thought I was reading somewhere that autotransformers are different when it comes to fault current. Please let me know
The available fault current on the primary side of the autotransformer is 6,700 amps.
The transformer is 32 kVA and I'm assuming 1.5% impedance. The available fault current at the elevator disconnect needs to be below 5,000 amps.
I would assume that the high voltage side of the transformer would reduce my available fault current and I could calculate it the same way that I would calculate fault current for a step down transformer. My secondary (480V) side is showing 1,359 amps. In my eyes, this would allow me to meet the short circuit current rating of the 5,000 amps listed on the elevator equipment.
I thought I was reading somewhere that autotransformers are different when it comes to fault current. Please let me know