ghelectricaloz
Member
I have been given the task of connecting 110 kW motor to auto transformer starter that had previosly ran this motor, at a different site with a different generator. I tested the control circuit and measured 277 V (3 phase) in the startup condition, and 415V in the run condition. Thinking this was working fine I connected the motor, on startup the star contactor (KM1) burnt out and the motor barely moved. This new generator is 140kVA, we knew this would be borderline to run the motor. On inspection found the star contactor was actually wired in a delta configuration, contrary to the drawings supplied. All other diagrams I can find seem to be the same (star connection in startup of KM1). Is the genie underpowered? why is KM1 connected in Delta? Mechanical load seems free. I need to get this plant running, help would be awesome, cheers GH