Good Afternoon,
I need to install an Auto Tx to step up the voltage of a 480VAC 3-ph 50kW generator to the connection voltage of the building 600VAC (Canada).
I am worried about neutral currents (The Wye's of Wye's) but Auto Tx's are a different beast!
The service Tx to the building is 347/600VAC Wye:g... should I connect the Neutral or not? What about the fact that the XO and HO are the same in an Auto Tx?
I think no Neutral connection and no ground connection on the XO/HO point but any advice or tips otherwise would be very helpful.
Thanks!!
I need to install an Auto Tx to step up the voltage of a 480VAC 3-ph 50kW generator to the connection voltage of the building 600VAC (Canada).
I am worried about neutral currents (The Wye's of Wye's) but Auto Tx's are a different beast!
The service Tx to the building is 347/600VAC Wye:g... should I connect the Neutral or not? What about the fact that the XO and HO are the same in an Auto Tx?
I think no Neutral connection and no ground connection on the XO/HO point but any advice or tips otherwise would be very helpful.
Thanks!!