S sheadpe New member Jun 23, 2010 #1 Are hard wired automatic flush valves for urinals, lavs, and sinks required to be wired to a GFCI circuit breaker in a commercial or institutional installation?
Are hard wired automatic flush valves for urinals, lavs, and sinks required to be wired to a GFCI circuit breaker in a commercial or institutional installation?
iwire Moderator Staff member Location Massachusetts Jun 23, 2010 #2 No ..................................
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer Jun 23, 2010 #3 In addition to agreeing with Bob's answer, I will add two things: Take a look at NEC 210.8(B). It's about receptacle outlets, not hard wired connections. Welcome to the forum.
In addition to agreeing with Bob's answer, I will add two things: Take a look at NEC 210.8(B). It's about receptacle outlets, not hard wired connections. Welcome to the forum.