A facility manager wants these installed :
http://www.wattstopper.com/products/details.html?id=105&category=62&type=Commercial
In out substation (26kv - 5 kv) as well as 2 other mechanical spaces (cooling tower substation 5kv - 480, with vfd's and mcc's), and in our chiller plant with pumps, vfd, and 3 line-ups of 5kv gear.
I'm against it citing:
OSHA 29CFR 1910.303(g)(1)(v)
? Illumination shall be provided for all working spaces about service equipment, switchboards, panelboards, and motor control centers installed indoors. Additional lighting fixtures are not required where the working space is illuminated by an adjacent light source. In electric equipment rooms, the illumination may not be controlled by automatic means only.
I don't believe we are both right or both wrong, referring to 'automatic means only'. These are installed in numerous penthouses with mechanical and electrical gear.
Your thoughts,
Jim
http://www.wattstopper.com/products/details.html?id=105&category=62&type=Commercial
In out substation (26kv - 5 kv) as well as 2 other mechanical spaces (cooling tower substation 5kv - 480, with vfd's and mcc's), and in our chiller plant with pumps, vfd, and 3 line-ups of 5kv gear.
I'm against it citing:
OSHA 29CFR 1910.303(g)(1)(v)
? Illumination shall be provided for all working spaces about service equipment, switchboards, panelboards, and motor control centers installed indoors. Additional lighting fixtures are not required where the working space is illuminated by an adjacent light source. In electric equipment rooms, the illumination may not be controlled by automatic means only.
I don't believe we are both right or both wrong, referring to 'automatic means only'. These are installed in numerous penthouses with mechanical and electrical gear.
Your thoughts,
Jim