Does anyone know of a good relay that will pull off automatic source transfer, with sync check built in? Here is the simplified single line:
Does anyone know of a good relay that will pull off automatic source transfer, with sync check built in? Here is the simplified single line:
An even better solution might be to use the right 50/51. The transfer function could be programmed or the manufacturer may offer templates. I have seen M-T-M transfers done with three SEL 751A Relays. It may be well worth your time to contact SEL. You have to have the 50/51s anyway.
https://selinc.com/products/751a/
Doesn't bus differential take care of 50/51?
I do not see the bus differential in the one line.
Bus differential should not respond to overcurrent. The same current entering the bus differential zone is leaving the bus differential zone.
But lets say I had a bush differential zone between source 1 and 2 and the transformer breaker. Would those not take care of 50/51?
87s are generally not concerned with the magnitude of current, just if it sums, current into the zone = current out of the zone, 50 A or 50,000 A. A good bus differential circuit is immune to a through fault. Over current relays would respond to the over current in their zone.
If your bus differential relay also has overcurrent functions like the SEL 587Z, you might be in business, if you spring for the extra CTs.
87B is expensive in this case with only three terminals and from the info, only one source works at the time.
but 87B could take care of that. even 50/51 with syn check or auto synch could do it.
the line side relays in my opinion is for switching, but it comes already with a standard OC relays, so three relays.
or, just use voltage relays..
Sent from my iPad using Tapatalk
huh? you could still do it in the things i have mentioned. for example lets say sel351a LOP is already a standard feature.
87b is really expensive... for me..
by the way, what voltage are we talking about? in low voltage, there are devices available for this scheme, it could even start a standby generator..
Sent from my iPad using Tapatalk
Of course, 87 is not supposed to care about current coming in and out of its sums. Thats the whole point of differential. Do not trip on anything outside of the zone of protection regardless of 1 amp or 63,000 amps.
You don't need over current to protect a bus bar. Thats why I am asking why I need 50/51 for the two source supply breakers.
I am not arguing that you need overcurrent protection, I do not have the details, only that the automatic transfer could be done with SEL 751s, or similar relays.
I have always thought that a high impedance bus differential relay was faster than a 50.