Pierre C Belarge said:
You are correct in the fact that it is "optional", I never have disputed this.
What I am saying is two fold.
1. the customer depends on the contractor's knowledge to install a product that will work.
2. Not all optional standbys are installed in homes, some are for businesses and they do in some way depend on the optional standby to help keep them up and running... again falling back to they depend on the contractor to install a product that works as explained to them.
all of the above is a design decision.
Of course, without a doubt I would communicate the problems to the customer and I would try to up sell the job to a high quality installation.
Now, back to my question.
Is it a proper/code installation to install a smaller rated generator than the load anticipated for an automatic transfer switch?
IMO yes it currently a NEC code complaint installation to use a smaller generator than the anticipated load connected to it.
If it was not we would not see the push for the change that is coming.
You do realize that if the change occurs in the NEC I will follow it as required but I will never agree that an optional generator should be sized per article 220.
My own home has a 100 amp 120/240 service or 24 KW.
Now for reasons of curiosity I ran everything in the house at the same time..window ACs, electric range, stove top, dryer lights, electronics, oil burner etc.
With all that on I had about 45 amps per leg at the meter using my true RMS Fluke 36 meter.
It is inconceivable to me that I if I chose to install a generator at all that the NEC would require me to buy a 24 KW or greater unit when it is not possible for the load to exceed 11 KW and that 11 KW is if I run everything at once.
Pierre can I ask you to address the safety difference in a generator being overloaded manually as compared to automatically?
Because the way this change is worded it appears the manufacturers believe there is a difference.