2000A service, 480/277V, 3PH, 4W.
Normal power feeders are coming in from a 1500kVA pad mounted transformer, through the ATS mounted inside the building and into the adjacent Main Switchboard with a 2000A Main Breaker.
We have a 1.5MVA generator backing up the entire building. Genset is protected by a 2000A breaker in the generator enclosure. Emergency power feeders are coming in through the ATS.
The ATS is NOT service entrance rated. Do I need a fused disconnect upstream on the line side of the ATS to meet 230.70 and/or 230.90? I thought the 2000A Main Breaker at the Switchboard covered this?