The Generac load-shedding is frequency based, and there is a hard limit of 8 load shedding devices; that includes the relay contacts built into the transfer switch. So if you used two of the internal HVAC relays, you could only use 6 additional load shedding modules.
The load shed modules each have an 8-position dial to set priority. When there is a power loss, all of the modules will open their contactors. Once the generator is running at 60hz, they’ll close. If the frequency drops below 60hz they will sequentially drop out starting at #8 until 60hz is maintained.
You could technically use more than 8 modules, but because they only measure 8 different frequencies, you would have multiple modules opening and closing at the same time. The relay contacts break the t-stat power. The modules have 2-pole contactors rated at 50A and 100A.