L leblar1 Member Location louisiana Oct 20, 2011 #1 Scenario, Business has a 2000A main service breaker. Standby generator will be 750KVA. The ATS would be sized at 2000A, correct? Thanks
Scenario, Business has a 2000A main service breaker. Standby generator will be 750KVA. The ATS would be sized at 2000A, correct? Thanks
ron Senior Member Location New York, 40.7514,-73.9925 Oct 20, 2011 #2 If there will be a 2000A breaker on the output of the generator, then yes.