I'm reviewing some shop drawings for a generator and ATS. The ATS Withstand Ratings are only for specific circuit breakers. The ATS doesn't have any withstand rating for use with current limiting fuses, and no ratings for "Any Breaker".
The problem is that the main breaker on the generator isn't one of the listed circuit breakers.
I know the generator will only provide a limited amount of fault current, usually less than 8-10X the generator current rating, which in this case, would probably be less than 5000 amps.
But still, doesn't the ATS need to be used with one of its listed breakers?
The problem is that the main breaker on the generator isn't one of the listed circuit breakers.
I know the generator will only provide a limited amount of fault current, usually less than 8-10X the generator current rating, which in this case, would probably be less than 5000 amps.
But still, doesn't the ATS need to be used with one of its listed breakers?