kriverswaters
Member
I have an installation of a 125KW, 120\208 Volt, three phase emergency generator & a "Service Entrance Rated" 400 Amp, Nema 1, Automatic transfer switch. They are planning on upgrading the existing 225 Amp, 120\208 Volt, three phase utility service to a 400 amp service within the next couple of years. As it is currently wired, the exsisitng 225 amp service comes in to a 400 Amp rated CT can, and then nipples to a 225 Amp main breaker distribution panel. The generator comes supplied with a 400 Amp breaker on the generator itself. The SER rated transfer switch has a 400 Amp Emergency generator breaker as well as a 400 Amp Normal Utility breaker. Do I have to add a 225 Amp disconnect between the transfer switch output and the Main Distribution panel (15'), or does the NEC 240.21 (2) cover this??? Paragraph "1" on this rule states that "the ampacity of the tap conductors is not less than one third of the rating of the overcurrent device protecting the feeder conductors." There never has been a "protecting device" on the feeder conductors, except the 225 Amp main in the distribution panel. Please clarify!!! Thanks