Hello everyone,
I'm working on a woodshop that has two 3ph table saws each with their own 1ph 240V 2hp dust collectors. I need to have the dust collectors turn on/off whenever the saws are turned on/off. Right now, the dust collectors are turned on via a simple mechanical manual ON/OFF contactor at the collector itself.
I figure I can replace that contactor with a magnetic contactor like a SqD 8910 DP12. I called SqD and the tech went right to a magnetic starter with thermal overload protection.
Do I need to make that leap ($$$) if the manual starter supplied with the dust collector sufficed? I want to run an SJ cord from the saw to the collector. Would tying one end into the load side of the saw's starter and the other into the coil of the collector's contactor be appropriate? Or maybe tap into the saw's A1 and A2 terminals? I'd like to use an 18 or 16ga SJ cord but would I need seperate circuit protection since the saw and collector are on 20A and 30A circuits?
Thanks for your input.
I'm working on a woodshop that has two 3ph table saws each with their own 1ph 240V 2hp dust collectors. I need to have the dust collectors turn on/off whenever the saws are turned on/off. Right now, the dust collectors are turned on via a simple mechanical manual ON/OFF contactor at the collector itself.
I figure I can replace that contactor with a magnetic contactor like a SqD 8910 DP12. I called SqD and the tech went right to a magnetic starter with thermal overload protection.
Do I need to make that leap ($$$) if the manual starter supplied with the dust collector sufficed? I want to run an SJ cord from the saw to the collector. Would tying one end into the load side of the saw's starter and the other into the coil of the collector's contactor be appropriate? Or maybe tap into the saw's A1 and A2 terminals? I'd like to use an 18 or 16ga SJ cord but would I need seperate circuit protection since the saw and collector are on 20A and 30A circuits?
Thanks for your input.