when a machine with a 480/400 autotransformer is turned on or off, lights fed from same panelboard as machine go off and back on. Machine is wired with a three-wire + ground SO portable cord drop. Electrician attempting to troubleshoot problem, connected a ground from the ground terminal to building steel. problem went away. Ultimately, equipment ground run with branch circuit is landed on the panelboard ground bus and the panelboard feeder equipment ground is landed on the switchboard ground bus supplying it and so on back to the grounding electrode system bus bar from which a grounding electrode conductor is connected to steel.
Any thoughts on why problem goes away when bonded locally to building steel. Since this local bond is connected to the equipment ground, potential should be zero. Am I missing something related to code or ground loops that prohibits this?