How's it going out there? Has anyone heard from 'mull982' in the last 2 days?
hdpeng said:How's it going out there? Has anyone heard from 'mull982' in the last 2 days?
Jraef said:Delving deeper then;
The LRC is 256A according to the nameplate, or are you assuming it is 600% of FLC? Because the 600% is a general rule of thumb, not an absolute. It depends upon your motor's design. (Edit: Must be nameplate, the math doesn't work out right after reading the original post)
Are you sure you don't have an issue with a CT ratio or something?
Are you using a Peak Hold feature on a meter to read that 314A value or the 369 display?
frenchelectrican said:one thing it kinda bother me why 9 seconds delay between the autotransformer and swiched to the DOL [ direct on line ] connections but i have a hunch but not sure it may ring in here right.
with the long delay the motor speed do drop down a bit and get the phase connect out of sych. by time the DOL contractors get on line and it draw just much current as plain jane DOL set up.
i will just suggest try to closen up the gap time from 9 seconds to something like 5 seconds or so. the reason i suggest that because it will really reduce the amout of the time the motor loose the speed when switching over.
Merci,Marc
weressl said:Marc, it is not DOL it is FVNR(Full Voltage Non-Reversing) and it would include SS(Solid State) contactors that are not reduced voltage starters.